Set A Questions 1 to 10
- 1
What does DC stand for in backflow prevention?
Explanation
Two independently acting check valves in series, with shut-offs and four test cocks so it can be field tested.
- 2
What differential must each check of a double check hold?
Explanation
Both checks carry the same criterion, and both must also close drip tight in the direction of flow.
- 3
How many test cocks does a double check valve assembly have?
Explanation
The four cocks straddle the two checks in the same arrangement as on an RP of the same size.
- 4
Which hazards may a double check be used on?
Explanation
It is not approved for a health hazard because it has no way of telling anybody that a check has failed.
- 5
Why is a double check unsuitable for a health hazard?
Explanation
An RP discharges visibly when it loses its margin. A double check simply stops protecting and says nothing.
- 6
What is a DCDA?
Explanation
The bypass meter catches small flows on a fire line, which usually means a leak or an unauthorised connection.
- 7
What must the bypass meter do during a test?
Explanation
It only has to move. Accuracy is not part of the criterion, because its job is detection rather than measurement.
- 8
Where is test cock three on a double check?
Explanation
The pair of cocks either side of a check is what lets the gauge straddle that check during the test.
- 9
Which two test cocks straddle check valve one?
Explanation
Cocks three and four straddle check valve two, which is why the hoses move between the two phases of the test.
- 10
What does drip tight mean for a check valve?
Explanation
A gauge reading that falls away to zero indicates a leak, and that fails the assembly whatever the number was beforehand.