Set B Questions 11 to 20
- 11
Why are the two checks described as independently acting?
Explanation
Independence is the whole design principle. Two barriers linked to one mechanism would be a single point of failure.
- 12
What loads the checks closed on a double check?
Explanation
The spring loading is why a double check will hold a small differential rather than relying on flow to shut it.
- 13
Which is the correct pressure loss comparison?
Explanation
The RP's higher first check loading and its relief mechanism both cost pressure, which matters on a marginal service.
- 14
Can a double check be installed in a vault?
Explanation
This is a genuine practical advantage of the double check, and it is why fire lines in vaults commonly use one.
- 15
What if a double check is fitted where a health hazard exists?
Explanation
The tester records what is fitted. Deciding the remedy belongs to the authority having jurisdiction and the owner.
- 16
Which reading order is used when testing a double check?
Explanation
Working from upstream to downstream keeps the hose moves logical and avoids disturbing a reading already taken.
- 17
What must happen downstream before a check reading is taken?
Explanation
The gauge is reading the difference between supply pressure above the check and atmosphere below it.
- 18
What is the effect of holding the gauge two feet below the reference?
Explanation
Two feet at 0.433 psi per foot is 0.87 psi. On a 1.0 psid criterion that is most of the margin.
- 19
Why does gauge elevation matter more on a double check?
Explanation
An error of 0.87 psi against a 5.0 criterion is annoying. Against a 1.0 criterion it decides the result.
- 20
What is correct when a double check reads zero on check one?
Explanation
Three of the four common causes of a zero reading are the tester rather than the valve, so the kit is checked first.