Set A Questions 1 to 10
- 1
What is being measured when a double check valve is tested?
Explanation
It is a static measurement. Nothing should be flowing through the assembly while a reading is taken.
- 2
Which pair of test cocks straddles check valve one?
Explanation
Check valve one sits between cocks two and three, exactly as it does on an RP of the same size.
- 3
Which pair of test cocks straddles check valve two?
Explanation
Moving the hoses one cock downstream is what shifts the gauge from the first check to the second.
- 4
What must be done to both shut-off valves during the test?
Explanation
The pressure inside then has to be held by the check valve rather than fed by the main.
- 5
What has to happen downstream before a reading is valid?
Explanation
The gauge is reading the difference between supply pressure above the check and atmosphere below it.
- 6
When is the reading taken?
Explanation
Reading while water is still moving gives a number that has nothing to do with the check valve.
- 7
What is the minimum acceptable reading for each check?
Explanation
Both checks carry the same 1.0 figure, and both must also be drip tight.
- 8
What does a reading that falls away to zero mean?
Explanation
Record it as leaked rather than as a low number. A leak fails the assembly whatever the reading was beforehand.
- 9
Where must the gauge centre line be held?
Explanation
On a 1.0 psid criterion, two feet of gauge error is most of the available margin.
- 10
How much does one foot of elevation error change a reading?
Explanation
One psi lifts water 2.31 feet, so one foot of water is 0.433 psi. Both numbers are worth knowing by heart.