Set C Questions 21 to 30
- 21
What is checked about the shut-off valves during a thorough test?
Explanation
A leaking shut-off is the single most common cause of readings that imitate component failures.
- 22
What is the correct condition of the assembly during a reading?
Explanation
A static measurement is the whole basis of the test. Any flow makes the number meaningless.
- 23
Which reading order avoids disturbing a result already taken?
Explanation
Working downstream keeps the hose moves logical and leaves each completed reading undisturbed.
- 24
What happens to a double check during backsiphonage?
Explanation
It has no vent and no air inlet. Everything depends on the two checks holding, which is why the hazard limit exists.
- 25
What is the correct result if check one shows 0.9 psid?
Explanation
The criterion is a minimum, not a target to round toward. There is no averaging between the two checks.
- 26
Can a strong reading on check two make up for a weak check one?
Explanation
They are independent barriers. Averaging them would defeat the reason there are two.
- 27
What should be done with the covers after a repair?
Explanation
An open body is an open path into the potable supply, whatever the checks inside it are doing.
- 28
What is the correct way to open a test cock?
Explanation
Opening a test cock quickly can slam the check and give a false observation.
- 29
What does a stable reading of 4.0 psid on a double check mean?
Explanation
There is no upper limit on a check valve differential. Higher is simply a healthier check.
- 30
Why does an RP first check use a higher criterion?
Explanation
The five psid figure and the three psid buffer together are what keep the relief valve closed in service.