Topic 11 · Gauges & Calibration
Set C Questions 21 to 30
- 21
What does a reading that falls immediately to zero suggest?
Explanation
Hoses on the wrong cocks, a needle valve left open and unpurged air are all tester faults rather than valve faults.
- 22
Why should a tester carry a spare set of hoses?
Explanation
A pinhole in a hose is very hard to see and produces a reading that drifts for no apparent reason.
- 23
What is a bleed-off valve assembly used for?
Explanation
It is standard on the SVB procedure and useful on a PVB with a leaking shut-off.
- 24
What does psid mean?
Explanation
The d matters. A criterion written in psid is a difference, not a pressure measured against the atmosphere.
- 25
How finely is a typical backflow gauge graduated?
Explanation
That resolution is what lets a tester distinguish a 4.8 from a 5.0 on a check valve one reading.
- 26
What is the risk of reading a needle from an angle?
Explanation
Reading square to the face is a habit worth building, because the criteria are decided by a fifth of a psi.
- 27
What if two readings of the same check disagree?
Explanation
Averaging hides a problem. Readings that will not repeat mean something in the setup is moving.
- 28
What does a digital test kit change about the criteria?
Explanation
A digital kit changes how the reading is captured, not what the assembly has to achieve.
- 29
Why is a temperature change in a hose a problem?
Explanation
A hose lying in direct sun is a real source of drift, and it is easily mistaken for a failing component.
- 30
What is checked on the kit before it leaves the workshop?
Explanation
The calibration date is the one that costs money when it is missed, because it invalidates the work retrospectively.