Topic 04 · Hazard & Assembly Selection
Set A Questions 1 to 10
- 1
Which assembly is required for a health hazard with backpressure?
Explanation
Only the RP vents its zone to atmosphere when a check begins to pass, so a failure announces itself instead of hiding.
- 2
Why is a double check not approved for a health hazard?
Explanation
Two checks in series are still two silent barriers. Nothing on a double check tells you when the first one stops sealing.
- 3
A pressure vacuum breaker protects against which condition only?
Explanation
This is the single most important limit on a vacuum breaker. Backpressure pushes straight past it whatever the hazard.
- 4
Irrigation with no pump and no injector is classified how?
Explanation
Irrigation is a health hazard because of what is in the soil, not because of the water going in. That surprises most candidates.
- 5
What changes when a fertiliser injector is added to irrigation?
Explanation
The injector is a pressure source. The answer moves from a vacuum breaker to a reduced pressure principle assembly.
- 6
How high above the highest downstream outlet must a PVB sit?
Explanation
Below the outlets there is no siphon for the air inlet to break, so the assembly cannot do its job however well it tests.
- 7
What is the minimum for a low hazard under backpressure?
Explanation
An RP is also acceptable, since a higher rated assembly can always be used in place of a lower one.
- 8
A carbonated beverage dispenser presents which combination?
Explanation
Carbon dioxide pushes back and carbonic acid leaches copper out of tubing, which is why copper piping is prohibited downstream.
- 9
Why is copper tube prohibited downstream of a carbonator?
Explanation
This is a recorded cause of illness in food service, and it is a favourite exam question.
- 10
A wet sprinkler with no additives and no booster is classed how?
Explanation
Stagnant water sitting in black steel is objectionable rather than dangerous. Add antifreeze or a booster and it changes.