Topic 04 · Hazard & Assembly Selection
Set B Questions 11 to 20
- 11
What is the minimum protection for a commercial dishwasher?
Explanation
Detergents make it a health hazard and the rinse water is pumped, so backpressure is possible.
- 12
Which two questions decide every assembly selection?
Explanation
Everything else follows from those two answers. Skipping the second one is how vacuum breakers end up on pumped systems.
- 13
An elevated tank filled through the top with no pump creates what?
Explanation
Elevation is a pressure source. A tank on a roof can push back down the fill line without any pump on site.
- 14
Which assembly may be used in place of any lower rated one?
Explanation
The RP protects against both causes at both hazard levels. The cost is a drain for the relief discharge and more pressure loss.
- 15
What does an RP need that a double check does not?
Explanation
Both assemblies need testing, shut-offs and a listing. Only the RP discharges water when it operates.
- 16
Where may an RP not be installed?
Explanation
A submerged relief port cannot vent, and it can siphon whatever is standing in the pit.
- 17
A cooling tower dosed with treatment chemicals requires what?
Explanation
Treated recirculating water under pump pressure is a health hazard with backpressure, which leaves one answer.
- 18
What is the correct protection for medical process equipment?
Explanation
Aspirators and process equipment can both contaminate the water and push back into it.
- 19
Why use a spill-resistant vacuum breaker instead of a PVB indoors?
Explanation
The spill resistance is the entire difference. The two carry identical pass criteria and identical limits on backpressure.
- 20
What is the minimum for a gravity fed food process with no chemicals?
Explanation
Objectionable rather than dangerous, and nothing downstream can make its own pressure. That is the least demanding case on the list.