Set C Questions 21 to 30
- 21
Which pressures must be used in the expansion tank formula?
Explanation
Using gauge pressure is the classic sizing error and it undersizes the tank badly.
- 22
What happens if a thermal expansion tank is undersized?
Explanation
A relief valve was never meant to operate daily, and it will eventually leak and then fail.
- 23
What is the water heater relief valve actually for?
Explanation
Using it as a daily expansion control is exactly what an undersized or missing tank does to it.
- 24
What is static pressure?
Explanation
Residual pressure is the same system with water moving, and it is always lower.
- 25
What is residual pressure?
Explanation
The difference between static and residual is what friction and the assembly have taken out of the system.
- 26
What is the effective opening of a half inch round outlet?
Explanation
For a shaped or non circular outlet it becomes the equivalent circular area instead.
- 27
Why does a fire flow cause backsiphonage?
Explanation
A hydrant flowing at a high rate can drop the surrounding pressure very quickly, which is a classic backsiphonage cause.
- 28
What creates backpressure in a building with no pump?
Explanation
Elevation is a pressure source. A tank on a roof pushes down the fill line with no pump involved.
- 29
Why is a barometric loop about thirty five feet tall?
Explanation
Since the atmosphere can only support about 34 feet of water, a loop above that height cannot be siphoned over.
- 30
What limits a barometric loop's usefulness?
Explanation
Thirty five feet of headroom rules it out almost everywhere except tall industrial buildings.