- 1
What is the usual minimum height from grade to an assembly?
Explanation
Low enough to work on and high enough that the relief port is not sitting in a puddle it could siphon back.
- 2
What is the usual maximum height to the centre line?
Explanation
Above that a tester cannot comfortably reach the test cocks or take the covers off.
- 3
How high must a PVB be above the highest downstream outlet?
Explanation
Six inches is the AVB figure. Confusing the two is one of the most common installation errors.
- 4
How high must an atmospheric vacuum breaker be above outlets?
Explanation
The AVB is six and the PVB is twelve. Both are measured above the highest downstream outlet.
- 5
Where must an AVB be fitted relative to control valves?
Explanation
Fitting it upstream leaves it under continuous pressure, which is exactly what it cannot tolerate.
- 6
Where may an RP not be installed?
Explanation
A submerged relief port cannot vent, and it can siphon whatever is standing in the pit.
- 7
Where must an RP relief port discharge?
Explanation
A direct connection makes the drain itself the cross-connection the assembly was fitted to eliminate.
- 8
Why must an RP have a drain able to take its full discharge?
Explanation
Undersized drainage is why so many RP installations end up flooding a plant room the first time they operate.
- 9
What is the usual requirement for orientation?
Explanation
Most assemblies are approved horizontal only, and the approval covers the position as much as the model.
- 10
What happens if a horizontal only assembly is fitted vertically?
Explanation
Spring loading helps, but the approval is written for a specific orientation and the listing does not carry over.