Topic 07 · PVB & SVB Construction
Set A Questions 1 to 10
- 1
What does PVB stand for?
Explanation
It is a testable assembly with a check valve, an air inlet, two shut-offs and two test cocks.
- 2
What are the two working components of a PVB?
Explanation
Both are spring loaded, and both carry a 1.0 criterion during the field test.
- 3
At what pressure must a PVB air inlet begin to open?
Explanation
The 2.0 figure belongs to an RP relief valve. Mixing the two up is a common error on the written exam.
- 4
What differential must a PVB check valve hold?
Explanation
Both PVB criteria are 1.0, which makes them easy to remember and easy to confuse with the RP figures.
- 5
Against what condition does a PVB give no protection?
Explanation
The other three are all backsiphonage, which is exactly what a PVB is for. Backpressure pushes straight past it.
- 6
How high above the highest downstream outlet must a PVB sit?
Explanation
Below the outlets there is no siphon for the air inlet to break. The installation height is part of how the assembly works.
- 7
What does SVB stand for?
Explanation
The spill resistance is what allows it to be used indoors where a PVB would discharge water during a test.
- 8
What is the practical difference between a PVB and an SVB?
Explanation
The criteria and the backpressure limitation are identical. Only the way the body is brought to atmosphere differs.
- 9
In what order are the two SVB components tested?
Explanation
The PVB reverses this and tests the air inlet first. The distinction is a favourite exam question.
- 10
In what order are the two PVB components tested?
Explanation
The SVB reverses it, because its vent valve lets the body come down to atmosphere without discharging water.