Topic 07 · PVB & SVB Construction
Set B Questions 11 to 20
- 11
How many test cocks does a PVB have?
Explanation
The SVB has one test cock and a vent valve, which is another way of telling the two apart at a glance.
- 12
What must be removed before testing a vacuum breaker?
Explanation
You have to be able to see the poppet move. That observation is half the test.
- 13
What does it mean if a PVB air inlet does not open during the test?
Explanation
Calling a shut-off fault an air inlet fault means replacing the wrong part. Work the shut-off and repeat before condemning anything.
- 14
What is checked after the body of a vacuum breaker is drained?
Explanation
Two things are asked of the air inlet. It must begin to open at 1.0 or higher, and it must open fully once the body empties.
- 15
Can a PVB be installed under continuous pressure?
Explanation
That is one of the main differences between a PVB and an AVB, and the reason a PVB can serve an irrigation zone valve.
- 16
What is a common application for a PVB?
Explanation
The other three all involve backpressure, which a vacuum breaker cannot resist whatever the hazard level.
- 17
Why does an SVB suit indoor installation?
Explanation
A PVB tested indoors will put water on the floor. The SVB was designed specifically to avoid that.
- 18
Which ASSE standard covers the pressure vacuum breaker assembly?
Explanation
1020 is the PVB and 1056 is the SVB. The two are closely related but they are separate standards.
- 19
Which ASSE standard covers the spill-resistant vacuum breaker?
Explanation
The SVB got its own standard because the vent arrangement changes both the construction and the test procedure.
- 20
May a vacuum breaker be used on a health hazard?
Explanation
Irrigation is the standard example. It is a health hazard and a PVB is acceptable because nothing downstream makes pressure.