Topic 07 · PVB & SVB Construction
Set C Questions 21 to 30
- 21
What happens to a PVB during a backsiphonage event?
Explanation
The check valve holds and the air inlet lets air in behind it. The two components work together, not in sequence.
- 22
What is the purpose of the canopy on a vacuum breaker?
Explanation
It must be refitted after a test. Leaving it off lets debris into the air inlet, which is what makes them stick.
- 23
Why can a PVB spit water in normal service?
Explanation
Measure the installation height first. A PVB below the outlets it protects is both spitting and useless.
- 24
What does a vacuum breaker have that a double check does not?
Explanation
The air inlet is the whole point. It is also why a vacuum breaker must sit above what it protects.
- 25
What does a vacuum breaker not have that a double check does?
Explanation
A vacuum breaker relies on one check plus an air inlet. A double check relies on two checks and nothing else.
- 26
What is the correct order for closing shut-offs on a PVB test?
Explanation
Closing downstream first stops water leaving the body while it is still pressurised, which is what the reading depends on.
- 27
How fast should the bleed be opened to find the air inlet point?
Explanation
A fast drop reads low. This is the same trap as the relief valve on an RP, and for the same reason.
- 28
What is recorded if a PVB air inlet does not open at all?
Explanation
It has to be ruled out first. A leaking number one shut-off produces exactly this symptom and is a different repair.
- 29
Can a PVB be repaired in place?
Explanation
A retest is required after any repair, and it is recorded as a retest rather than as the original test.
- 30
Which is true of both a PVB and an SVB?
Explanation
The shared limitation is the important one. Everything else about them differs in detail.