Topic 10 · PVB & SVB Field Test
Set B Questions 11 to 20
- 11
Where is the high hose connected for the PVB check valve test?
Explanation
Test cock one is upstream of the check, and test cock two is vented so the body sits at atmosphere.
- 12
What is opened to bring the PVB body to atmosphere?
Explanation
When water stops draining from test cock two the differential across the check can be read.
- 13
When is the PVB check valve reading taken?
Explanation
Reading while water is moving gives a number that has nothing to do with the check valve.
- 14
What is used on an SVB in place of a second test cock?
Explanation
That is the whole design difference. The body vents in a controlled way rather than spilling from the air inlet.
- 15
What is fitted to the SVB test cock before the hose?
Explanation
The bleed-off gives a way to trim the flow if the number one shut-off turns out to be passing water.
- 16
What is opened to bring an SVB body to atmosphere?
Explanation
This is what makes the assembly spill resistant, and it is why an SVB can be tested indoors.
- 17
What does water running from an SVB vent at more than a drip mean?
Explanation
The bleed-off is opened slowly until the vent is down to a drip, and then the reading is taken.
- 18
What if the SVB vent flow cannot be brought down to a drip?
Explanation
A shut-off that cannot isolate makes the assembly untestable, and that is a different repair from a component failure.
- 19
Why must the kit stay at the same level for both SVB tests?
Explanation
The SVB procedure is deliberately written so both readings are taken from one position.
- 20
At what level should the kit be held for an SVB test?
Explanation
For a PVB the reference is the air inlet during the first test and test cock two during the second.