Topic 10 · PVB & SVB Field Test
Set C Questions 21 to 30
- 21
What does a PVB air inlet that never opens usually indicate?
Explanation
Work the shut-off open and closed to reseat it and repeat. Calling it an air inlet fault replaces the wrong part.
- 22
What is the alternative way to drop pressure if the shut-off leaks?
Explanation
If test cock one is fully open and the inlet still has not moved, the shut-off itself needs repair or replacement.
- 23
What is recorded if the air inlet does not open at all?
Explanation
Ruling out the shut-off first is what separates an assembly fault from a valve fault.
- 24
What must be done to the canopy at the end of the test?
Explanation
Leaving it off lets debris into the air inlet, which is one of the main reasons poppets stick.
- 25
In what order are the shut-offs reopened at the end of an SVB test?
Explanation
Opening the downstream valve first can pull the body down and lift the air inlet.
- 26
Which criteria apply to both a PVB and an SVB?
Explanation
Identical numbers for both assemblies. Only the order of the two tests differs.
- 27
How many test cocks does an SVB have?
Explanation
One test cock plus a vent valve. Counting the cocks is the quickest way to identify which assembly is in front of you.
- 28
Why can a PVB not be tested indoors without preparation?
Explanation
That is exactly the problem the spill-resistant version was designed to solve.
- 29
What should the tester note about the installation height?
Explanation
A vacuum breaker below the outlets it protects cannot work, however well it tests.
- 30
What does a PVB that spits water in service usually indicate?
Explanation
Measuring the height first is the right move. No amount of rebuilding will fix a wrong installation.