Set A Questions 1 to 10
- 1
What does RP stand for?
Explanation
The name describes how it works. The zone between the checks is deliberately held below the supply pressure.
- 2
What are the main components of an RP assembly?
Explanation
The relief valve and the four test cocks are what distinguish it from a double check of the same size.
- 3
What is the reduced pressure zone?
Explanation
Everything the relief valve does is about protecting that one space. Its whole purpose is to be lower than the supply.
- 4
What does the differential relief valve sense?
Explanation
It does not communicate with the checks at all. It only cares about how far the zone sits below the supply.
- 5
At what differential must the relief valve open?
Explanation
The 5.0 figure belongs to check valve one, and 3.0 is the buffer between the two. Mixing them up is a common error.
- 6
What differential must check valve number one hold?
Explanation
It must also sit at least 3.0 psid above wherever the relief valve opened, which is a separate requirement.
- 7
What is the buffer requirement on an RP?
Explanation
An assembly reading 5.5 across check one with a relief opening at 3.5 has two passing numbers and a failing buffer of 2.0.
- 8
An RP reads 5.5 on check one and 3.5 at the relief. Result?
Explanation
This is exactly the case a simple subtraction calculator gets wrong. Both individual numbers pass and the assembly still fails.
- 9
What does check valve number two on an RP resist?
Explanation
It is tested for tightness against backpressure rather than for a minimum differential during the main phase of the test.
- 10
Why does an RP announce its own failure?
Explanation
That visible discharge is the reason an RP is acceptable on a health hazard and a double check is not.