Set C Questions 21 to 30
- 21
What is the typical pressure loss characteristic of an RP?
Explanation
The relief valve mechanism and the higher spring loading on check one both cost pressure, which matters on marginal services.
- 22
What should a tester note about the direction of flow?
Explanation
An assembly fitted backwards produces readings that look exactly like component failures.
- 23
What is the purpose of the two shut-off valves on an RP?
Explanation
A leaking number one shut-off is the single most common cause of readings that imitate component failures.
- 24
Which failure imitates almost every other fault on an RP?
Explanation
It keeps feeding the assembly during the test so nothing behaves as it should. Suspect it before condemning any part.
- 25
What material are RP bodies commonly made from?
Explanation
Size and pressure class drive the material choice, and the internal trim is usually bronze or stainless whatever the body is.
- 26
What is the function of the sensing passage on a relief valve?
Explanation
A blocked sensing passage stops the relief valve responding at all, which reads as a relief valve that will not open.
- 27
What does an RP relief valve dripping occasionally mean?
Explanation
Thermal expansion in a newly closed system and a small piece of debris on the first check seat are the other usual causes.
- 28
Why must an RP be accessible for testing?
Explanation
Clearance for a gauge, two hands and the covers is part of an approved installation, not an optional convenience.
- 29
What is the usual minimum height of an RP above grade?
Explanation
Low enough to work on and high enough that the relief port is not sitting in a puddle it could siphon back.
- 30
What happens to an RP in freezing conditions?
Explanation
Heat tape wrapped over a relief port is worse than no heat tape, because it blocks the vent the assembly depends on.