Set C Questions 21 to 30
- 21
In what order are the bleeds closed when reading check valve two?
Explanation
The same order as the first phase: the high bleed first, then the low bleed, slowly. Closing the low one first traps pressure on the low side, and that is what catches people.
- 22
What is the minimum differential for check valve two on an RP?
Explanation
Check valve two carries the same numeric criterion as a check on a double check assembly.
- 23
What is done with the needle valves at the end of a test?
Explanation
Draining stops the kit freezing in the truck and keeps the gauge honest until its next calibration.
- 24
How is the outlet shut-off valve opened at the end of a test?
Explanation
Opening fast sends a surge downstream and can lift debris into fixtures the tester was not hired to fix.
- 25
What does it mean if the relief valve will not open during a test?
Explanation
A blocked sensing passage and a genuinely seized valve are the other causes, but the shut-off is checked first.
- 26
What should be recorded about the assembly before testing?
Explanation
The inspection is part of the test. An assembly fitted backwards produces readings that look like component failures.
- 27
How many separate readings does a full RP test produce?
Explanation
The relief opening point and the check valve one differential are the numbers. The rest are observations.
- 28
What is the purpose of the vent hose on an RP test?
Explanation
Without it there is no way to ask check valve two the question the hazard depends on.
- 29
When is the vent control closed during the backpressure phase?
Explanation
Leaving it open where check two held is deliberate, because the next readings depend on that path.
- 30
What does the tester do if the assembly fails?
Explanation
The retest is recorded as a retest after repair, not as the original test, and the due date runs from the passing result.