Set D Questions 31 to 40
- 31
Why does a failed test not reset the annual due date?
Explanation
Treating a failure as a completed annual is how an assembly sits broken for a year.
- 32
What has to be true of the gauge before any reading is taken?
Explanation
An out of calibration gauge invalidates every reading taken with it, and it is discovered months later.
- 33
What should the tester do if the supply pressure is unusually low?
Explanation
Low supply pressure can prevent check valve one developing five psid even when the check itself is sound.
- 34
Where should the gauge be held during the RP test?
Explanation
Every foot off level shifts the reading by 0.433 psi, and that matters even against a five psid criterion.
- 35
What does the reduced pressure zone contain in normal service?
Explanation
The margin between supply and zone is what keeps the relief valve closed.
- 36
What is the effect of closing test cock two during the shut-off check?
Explanation
The step is written as closing test cock two and watching, because a rise can then only come from downstream.
- 37
What is a common reason for a bouncing needle during an RP test?
Explanation
Flow still moving through the assembly and a partly open needle valve are the other two usual causes.
- 38
What must be done before the assembly is left at the end of a visit?
Explanation
Leaving a test cock open is an open cross-connection, and it is a mistake that has ended careers.
- 39
Which reading does a candidate most often misplace on a report?
Explanation
Three numeric criteria appear in one test at 2.0, 3.0 and 5.0, and they belong to different components.
- 40
What is the correct description of the RP test sequence?
Explanation
The order exists so that each step leaves the assembly in the state the next step needs.