Topic 14 · Troubleshooting & Repair
Set A Questions 1 to 10
- 1
Which single fault imitates almost every component failure?
Explanation
It keeps feeding the assembly during the test, so nothing behaves as it should. Suspect it first, always.
- 2
An RP relief valve discharges continuously. What is checked first?
Explanation
Discharge that stops when a downstream valve closes is a hydraulic problem, not a component failure.
- 3
What causes an RP relief valve to drip only now and then?
Explanation
Ask whether a heater or a check valve was fitted recently. Thermal expansion in a newly closed system shows up exactly like this.
- 4
An RP relief valve will not open during the test. What is most likely?
Explanation
A blocked sensing passage and a genuinely seized valve are the other causes, but the shut-off is checked first.
- 5
A check valve reads low but does not leak. What is the likely cause?
Explanation
Reading again after a gauge reset matters too, because disc compression can make an earlier reading look high.
- 6
A gauge falls straight to zero. What should be considered?
Explanation
Three of those four causes are the tester rather than the valve, so the kit is checked before the assembly.
- 7
The needle bounces and will not settle. What should be done?
Explanation
Air in the hoses and flow still moving through the assembly are the two usual causes, and purging fixes both.
- 8
The downstream side will not come down to atmosphere. Why?
Explanation
A second service feeding the same downstream piping is common on older commercial buildings.
- 9
A PVB air inlet never opens as pressure falls. What is checked first?
Explanation
Work the shut-off open and closed to reseat it and repeat before condemning the air inlet.
- 10
A PVB spits water in normal service. What is measured first?
Explanation
A PVB below the outlets it protects is both spitting and useless, and no rebuild will fix a wrong installation.