Water keeps running from an SVB vent during the check test. Why?
Explanation
Open the bleed-off slowly until the vent is down to a drip, then take the reading.
- 12
Readings drift between two attempts minutes apart. Why?
Explanation
Every foot the gauge moves shifts the reading by 0.433 psi, which is most of the margin on a 1.0 criterion.
- 13
What does a relief valve opening below 2.0 psid indicate?
Explanation
It means the zone loses its margin too easily, and the assembly is no longer announcing failure reliably.
- 14
What does a check valve one reading of 4.5 psid on an RP mean?
Explanation
The buffer requirement is separate and additional. Failing the 5.0 minimum ends the matter on its own.
- 15
An RP reads 6.0 on check one and 3.5 at the relief. What is the verdict?
Explanation
Six minus three point five is two point five, which is below the three psid buffer requirement.
- 16
What is the first move when a component appears to have failed?
Explanation
Replacing perfectly good rubber because a shut-off was passing is the most expensive mistake in the trade.
- 17
What causes a fouled check valve seat?
Explanation
A strainer upstream helps, but it has to be accessible and it has to be cleaned.
- 18
What is the effect of a blocked relief valve sensing passage?
Explanation
It presents as a relief valve that will not open, which is the same symptom as a leaking upstream shut-off.
- 19
What does a stuck air inlet poppet usually result from?
Explanation
Debris after a canopy is left off is the other frequent cause, and refitting it after every test avoids that.
- 20
Which symptom points to backpressure entering an RP zone?
Explanation
One drip can be residual water. Two after a proper reset is check valve two failing.