Topic 14 · Troubleshooting & Repair
Set C Questions 21 to 30
- 21
What should be done before condemning check valve two?
Explanation
The reset is what separates residual water in the zone from genuine backpressure getting past the check.
- 22
What does an assembly fitted backwards look like on a gauge?
Explanation
Checking the flow arrow before connecting the gauge saves an hour and a wrong diagnosis.
- 23
What is the effect of a partly blocked strainer upstream?
Explanation
It looks like a supply pressure problem, and the assembly itself is entirely innocent.
- 24
Why can low supply pressure fail a good RP?
Explanation
Noting the supply pressure on the report is what lets somebody else see why the assembly read the way it did.
- 25
What if the same assembly fails twice after a genuine repair?
Explanation
A repeat failure after a genuine repair usually means the cause is outside the assembly body.
- 26
What is the usual cause of a leaking test cock?
Explanation
Flushing the cocks properly before connecting is what keeps debris off both the seat and the gauge.
- 27
What is the correct action when a repair kit has been fitted?
Explanation
The due date runs from the passing result, and the retest is what produces that result.
- 28
What makes a check valve read higher than it will hold in service?
Explanation
That is exactly why the gauge is reset on the low bleed before the check valve one number is taken.
- 29
What does discharge that stops on downstream demand indicate?
Explanation
That is a hydraulic problem with the service, and rebuilding the assembly will not solve it.
- 30
What is the risk of diagnosing from a single reading?
Explanation
Repeating a reading and getting the same number is what turns a measurement into a diagnosis.