- 31
Running the circulation pump only during opening hours is
Explanation
Chemical feed, filtration and turnover all stop with the pump, and the water is not being treated while the venue is closed.
- 32
A pump that has lost prime will usually
Explanation
A centrifugal pump cannot move air. The motor runs on with nothing happening, and running dry damages the seal.
- 33
Air bubbles appearing at the return inlets usually indicate
Explanation
The suction side is below atmospheric pressure, so a leak there draws air in rather than letting water out.
- 34
A variable speed pump run at a lower speed will
Explanation
Lower speed means lower flow. The energy saving is real but the turnover requirement still has to be met.
- 35
A flow turndown system is permitted to reduce flow only if
Explanation
The saving is allowed only where the water quality it protects is demonstrably still being achieved.
- 36
Water drawn from the venue to supply a water feature
Explanation
Unfiltered water cannot count. Water that leaves and returns without being treated has done nothing for the turnover.
- 37
The volume used when calculating turnover should include
Explanation
The whole system volume has to be circulated, and the model code defines it as the venue and any surge or balance tank (MAHC 4.7.1.10.3.2). Leaving out the surge tank understates the flow the venue needs.
- 38
A 4 inch schedule 40 line carrying 300 gallons per minute is running at about
Explanation
That is above the 6 feet per second suction limit, so this flow would need a larger pipe on the suction side.
- 39
The correct fix for water travelling too fast through a suction line is to
Explanation
Throttling suction risks cavitation, and a smaller pump would fail the turnover. Larger pipe solves it without either problem.
- 40
A gate valve is intended to be used
Explanation
Throttling a gate valve wears the seat and the gate. A butterfly or a globe valve is the right choice where flow is being trimmed.