Before brazing on any system containing refrigerant residue, the technician must
Explanation
This has always been correct practice, because heating refrigerant produces toxic decomposition products. With an A2L there is the additional risk of igniting what remains.
- 12
Which gas is flowed through tubing while brazing to prevent internal oxidation?
Explanation
Nitrogen flowing at a low rate displaces oxygen and stops black copper oxide flaking off inside the tube. Those flakes go on to block metering devices.
- 13
A2L equipment installed indoors commonly includes
Explanation
The sensor detects a leak and triggers mitigation, typically running the indoor blower to disperse refrigerant below its flammable limit and locking out ignition sources.
- 14
When an A2L leak detection system activates, the equipment typically
Explanation
Running the blower is deliberate and can seem counter-intuitive. Circulating air keeps the concentration below the lower flammability limit, which is far safer than letting refrigerant pool.
- 15
Disabling or bypassing an A2L leak sensor to keep a system running is
Explanation
The sensor is a condition of the equipment listing and often of the SNAP approval. Bypassing it removes the mitigation the whole safety case depends on.
- 16
The maximum refrigerant charge permitted in an A2L system serving an occupied space depends primarily on
Explanation
Charge limits are set so that a full leak into the smallest served room cannot reach the lower flammability limit. A smaller room therefore permits a smaller charge.
- 17
Which is a genuine ignition risk when working on an A2L system?
Explanation
The concern is any source of a spark or flame inside the flammable range near a leak. Rated tools and good ventilation are what keep the concentration and the ignition source apart.
- 18
R-454B has a temperature glide of roughly one to three degrees Fahrenheit. This means it should be
Explanation
Any zeotropic blend must be removed from the cylinder as liquid. Drawing vapour takes the more volatile component out first and leaves the wrong mixture behind.
- 19
Superheat on a blend such as R-454B is calculated using
Explanation
Superheat is measured from the dew point, where the last liquid has finished boiling. Using the bubble point instead inflates the answer by the whole glide.
- 20
Subcooling on a blend such as R-454B is calculated using
Explanation
Subcooling is measured from the bubble point, where liquid is about to begin boiling. Superheat uses dew and subcooling uses bubble, and swapping them is the most common blend error.