Topic 03 · A2L Refrigerants & the 2025 Transition
Set E Questions 41 to 45
- 41
Compared with recovering R-410A, recovering R-454B requires
Explanation
The procedure is familiar; the equipment rating and the surrounding precautions are what change. The venting prohibition applies exactly as it does to any other refrigerant.
- 42
Venting an A2L refrigerant because it has a low global warming potential is
Explanation
The prohibition on venting substitutes has applied since 1995 and does not depend on how harmful the refrigerant is. A low warming potential is not an exemption.
- 43
Which tool change is most often needed when moving from A1 to A2L service work?
Explanation
It is the powered and connecting equipment that changes, because those are the potential ignition sources and the physical interfaces to the cylinder.
- 44
Vacuum pumps used on A2L systems should be
Explanation
The pump draws refrigerant vapour through its motor compartment and exhausts it into the room. An unrated pump places a motor and its brushes directly in that path.
- 45
The best summary of what changes for a technician moving to A2L refrigerants is
Explanation
Superheat, subcooling, evacuation and recovery all work as before. What is new is treating the refrigerant as a fuel: rated tools, ventilation, ignition control and charge limits.