Topic 04 · Core: Leak Repair & Records
Set B Questions 11 to 20
- 11
How long must leak repair and refrigerant addition records be retained?
Explanation
Three years is the standard Section 608 retention period, and the records must be available to EPA on request.
- 12
A soap bubble solution is used to find leaks. Its main limitation is that it
Explanation
Bubbles are cheap and definitive when they work, but a slow leak may take a long time to raise a bubble and a buried joint cannot be reached.
- 13
An electronic leak detector should be calibrated and checked
Explanation
A detector that has lost sensitivity gives a clean result on a leaking system, which is worse than no detector at all because it produces false confidence.
- 14
Fluorescent dye leak detection requires
Explanation
Incompatible dye can attack seals and void equipment warranties. Many manufacturers specify which dyes, if any, are acceptable in their systems.
- 15
Pressure testing a system for leaks should use
Explanation
Nitrogen is inert and dry. Oxygen mixed with refrigerant oil can detonate, and compressed air introduces moisture as well as being an oxidiser.
- 16
Using oxygen to pressure test a refrigeration system is
Explanation
Oxygen under pressure in contact with hydrocarbon oil can ignite violently. It is one of the few genuinely lethal mistakes available in this trade.
- 17
The maximum pressure used when leak testing must not exceed
Explanation
The data plate gives the tested pressures for each side. A nitrogen cylinder holds well over 2,000 psig, so a regulator and attention to the plate are both essential.
- 18
A nitrogen cylinder must always be used with
Explanation
Full cylinder pressure would burst most refrigeration components instantly. The regulator sets a safe working pressure and the relief protects against regulator failure.
- 19
Where do leaks most commonly occur in a split system?
Explanation
Anywhere the system was joined or opened is where it leaks. Straight tube rarely fails unless it has been rubbed through or corroded.
- 20
Formicary corrosion in evaporator coils is caused by
Explanation
It produces pinhole leaks that are extremely hard to find and are usually attacked from the air side rather than the refrigerant side.