Topic 04 · Core: Leak Repair & Records
Set E Questions 41 to 45
- 41
Which is the best evidence that a system has a leak rather than having been undercharged at install?
Explanation
One low reading proves nothing about its cause. A pattern of additions over time is what distinguishes a leak from a one-off commissioning error.
- 42
When a leak is found in a system containing a zeotropic blend, the correct approach is to
Explanation
The remaining charge no longer has the correct composition, so a full recharge is the only way to restore it.
- 43
Pressurising a low pressure chiller above its rupture disc setting during a leak test
Explanation
Low pressure machines carry rupture discs set around fifteen pounds per square inch. Exceeding that vents the charge, which is both a loss and a violation.
- 44
A refrigerant leak in an occupied space is a hazard mainly because
Explanation
Asphyxiation is the primary hazard for most refrigerants. Flammability adds a second hazard for A2L and A3 fluids but does not replace the first.
- 45
The most reliable long term way to reduce refrigerant emissions from a building is
Explanation
Emissions are dominated by leaks rather than by service losses. Prompt repair backed by good records is what the whole regulatory structure is trying to produce.