Topic 02 · Core: Recovery, Recycling & Reclaim
Set B Questions 11 to 20
- 11
Refilling a disposable refrigerant cylinder is
Explanation
Disposable cylinders are single use, have no protective valve cap and are not built or tested for refilling. Refilling one is a DOT violation and a well documented cause of injury.
- 12
How often must a refillable recovery cylinder be hydrostatically retested?
Explanation
Five years is the standard DOT retest interval, and the test date is stamped into the collar. A cylinder past its date must not be filled or transported.
- 13
Before recovering into a used cylinder, the technician should
Explanation
Recovering a second refrigerant into a cylinder that already holds another creates a mixture nobody can reclaim, and the reclaimer will charge to dispose of it.
- 14
Mixing two different refrigerants in one recovery cylinder
Explanation
Mixed refrigerant cannot be separated economically. It has to be incinerated, and the disposal fee usually exceeds the value of everything in the cylinder.
- 15
Recovering liquid rather than vapour is preferred on a large system because
Explanation
Liquid recovery moves the bulk of the charge quickly. The last of it always has to come out as vapour, which is the slow part of any recovery.
- 16
Placing a recovery cylinder in a tub of cool water during recovery
Explanation
Recovery slows as the cylinder warms and its pressure rises. Cooling the cylinder lowers that pressure and restores the difference the recovery machine is working against.
- 17
Recovery slows down noticeably as the job goes on mainly because
Explanation
Recovery depends on a pressure difference. As that difference closes from both ends, the flow drops, which is why cooling the cylinder helps so much.
- 18
Non-condensable gases in a recovery cylinder are usually
Explanation
Air is the usual non-condensable. It raises cylinder pressure above what the refrigerant alone would produce at that temperature, and it does not condense at any normal pressure.
- 19
How can non-condensables in a recovery cylinder be detected?
Explanation
Let the cylinder stand until it reaches ambient temperature, then compare the reading against the chart. Pressure noticeably above the chart figure means air is present.
- 20
When purging non-condensables from a recovery cylinder, the cylinder should be
Explanation
Air collects above the liquid, so a slow purge from the top releases mostly air. Purging fast or from the bottom releases refrigerant, which is a venting violation.