Recovery equipment manufactured on or after 15 November 1993 must be
Explanation
Certification is by an approved testing laboratory such as UL or AHRI, against the recovery efficiency required for the appliance type.
22
A technician servicing appliances must have recovery equipment that is
Explanation
The certification has to match the work: small appliance equipment for Type I, high pressure equipment for Type II, and so on.
23
What is the purpose of a filter drier in a recovery or recycling machine?
Explanation
Moisture combines with refrigerant and oil to form acids that attack windings and copper. A filter drier removes both moisture and the acid already formed.
24
After a compressor burnout, the recovered refrigerant should be
Explanation
Burnout refrigerant carries acid and combustion products. Putting it back guarantees a second failure, so it goes for reclaim and the system is cleaned up before recharging.
25
An acid test on the refrigerant oil is used to determine
Explanation
Acid in the oil is the fingerprint of a burnout or of moisture that has broken the refrigerant down. It dictates how thoroughly the system must be cleaned before recharging.
26
The push-pull method of recovery is best suited to
Explanation
Push-pull moves liquid directly from the system to the cylinder and is typically used above roughly ten to fifteen pounds. It cannot remove the last of the charge, so vapour recovery finishes the job.
27
In push-pull recovery, the recovery machine
Explanation
The machine lowers the cylinder pressure and raises the system pressure, and that difference pushes liquid along the transfer hose. The machine never handles the liquid itself.
28
Push-pull recovery must be stopped when
Explanation
Once liquid stops flowing, push-pull is doing nothing useful and the remaining charge must be recovered as vapour. The 80 percent limit applies throughout.
29
Why should hoses used for recovery be as short as practical and fitted with low loss fittings?
Explanation
Every foot of hose is both restriction and trapped refrigerant. Low loss fittings close as the hose is removed so that the trapped charge is not vented.
30
A system-dependent, or passive, recovery device relies on
Explanation
Passive recovery has no pump of its own. It uses the appliance's pressure or its working compressor, which is why it is limited to small appliances.