Topic 05 · Core: Safety, Cylinders & Disposal
Set E Questions 41 to 45
- 41
Nitrogen regulators used for refrigeration work should have
Explanation
The cylinder gauge shows what is left and the delivery gauge shows what the system is receiving. The relief valve protects the system if the regulator fails open.
- 42
The reason refrigerant should never be used to blow out debris or clean a surface is that
Explanation
It is a knowing release with no recovery attempt, which is the clearest form of venting violation there is.
- 43
When a refrigerant alarm sounds in a machinery room, the correct first action is to
Explanation
Entering an alarming space to investigate is how technicians are injured. Ventilate first, test the atmosphere, then enter with appropriate protection.
- 44
Refrigerant vapour concentrating at floor level in a basement plant room is a hazard because
Explanation
Low level pooling is why low level sensors and low level ventilation are required. Most refrigerants have no useful smell to warn anyone.
- 45
The single most important safety habit when servicing refrigeration equipment is
Explanation
Nearly every serious refrigerant incident traces back to opening a charged system or assuming the wrong refrigerant. Both are avoidable before a wrench is picked up.