Topic 09 · Refrigerants, Blends & Oils
Set B Questions 11 to 20
- 11
Latent heat is heat that
Explanation
The entire refrigeration cycle depends on latent heat. Boiling in the evaporator and condensing in the condenser move far more heat than temperature change alone could.
- 12
Sensible heat is heat that
Explanation
Sensible heat is what a thermometer reads. Superheat and subcooling are both sensible heat added to or removed from saturated refrigerant.
- 13
Mineral oil is compatible with
Explanation
Mineral oil circulates and returns properly with CFCs and HCFCs. It does not mix with HFCs, which is why POE oil exists.
- 14
Polyolester oil is used with
Explanation
POE mixes with HFCs so the oil returns with the refrigerant. Its major drawback is that it absorbs moisture from the air extremely quickly.
- 15
POE oil containers must be kept sealed because
Explanation
Moisture in POE forms acid inside the system. Small sealed containers are preferred over large ones for this reason.
- 16
A drop-in replacement refrigerant, strictly speaking
Explanation
The term is marketing rather than engineering. Almost every retrofit requires at least an oil change and often a metering device change.
- 17
Retrofitting an R-22 system to an HFC blend usually requires
Explanation
The oil is the main issue, since mineral oil will not return with an HFC. The system must also be relabelled so the next technician knows what is in it.
- 18
After a retrofit, the appliance must be
Explanation
Without a label, the next technician charges the wrong refrigerant into the wrong oil, and the failure that follows is entirely avoidable.
- 19
R-410A operates at pressures roughly what compared with R-22?
Explanation
The higher pressures are why R-410A equipment, gauges and hoses are rated differently, and why R-22 equipment must never be used with it.
- 20
Charging R-410A into a system designed for R-22 would
Explanation
Two independent failures: the pressure rating and the oil. Either alone would be enough to destroy the system.