Topic 09 · Refrigerants, Blends & Oils
Set D Questions 31 to 40
- 31
A refrigerant's ability to absorb heat when it boils is measured by its
Explanation
A high latent heat means a smaller mass flow moves the same cooling. Ammonia's exceptionally high value is one reason it persists industrially.
- 32
Moisture in a refrigeration system is harmful because it
Explanation
Two separate failures follow: acid attacks windings and copper, and ice blocks the restriction intermittently.
- 33
The maximum acceptable moisture content of reclaimed refrigerant is set by
Explanation
AHRI 700 specifies limits for moisture, acid, non-condensables, high boiling residue and particulates, and reclaim requires laboratory verification against it.
- 34
A refrigerant cylinder colour code identifies
Explanation
Colours are a helpful cue but never proof. The label and, where doubt exists, a refrigerant identifier are what confirm the contents.
- 35
Adding R-134a to a system containing R-12 residue and mineral oil will typically
Explanation
The oil logs in the evaporator and never returns to the compressor. Proper conversions flush the mineral oil out and replace it with POE.
- 36
A refrigerant with a high discharge temperature such as R-32 requires attention to
Explanation
Excessive discharge temperature breaks down oil and damages valves. It is one reason R-454B, which runs cooler, is often preferred to pure R-32.
- 37
The critical temperature of a refrigerant is
Explanation
Condensing must happen below this temperature. It is why CO2 systems in hot climates run transcritical, with a gas cooler rather than a condenser.
- 38
Which of the following is NOT a legitimate reason to change refrigerants in a system?
Explanation
Refrigerant substitution must follow the SNAP listing for that end use and the manufacturer's approval. Price alone is not a basis for it.
- 39
Using a refrigerant not listed as acceptable under SNAP for that end use is
Explanation
SNAP listings are end use specific, so a refrigerant acceptable in commercial refrigeration is not automatically acceptable in residential air conditioning.
- 40
Hydrocarbon refrigerants have been marketed as R-22 replacements for residential systems. Using them there is
Explanation
EPA has issued specific warnings about this. The equipment has no leak mitigation and its electrics are potential ignition sources.