Total external static pressure is measured
Explanation
The return reads negative because the blower is pulling on it. Adding the sizes of the two readings gives what the blower is actually working against.
- 2
A typical residential air handler is rated for a total external static pressure of about
Explanation
Half an inch of water column is the common rating. Field surveys routinely find installed systems running at double that.
- 3
A total external static pressure well above the blower rating causes
Explanation
A PSC motor simply moves less air. An ECM tries to hold its target and burns itself out attempting it.
- 4
A high return side static pressure most often indicates
Explanation
Splitting the total into its two halves is what makes the measurement useful. High return points at the filter and return path; high supply points at the coil and supply ducts.
- 5
The airflow equation for sensible heat uses the constant
Explanation
The 1.08 combines air's specific heat, its density and sixty minutes per hour, at sea level conditions.
- 6
At high altitude, the sensible heat constant of 1.08
Explanation
Thinner air carries less heat per cubic foot, so more cubic feet are needed for the same duty. Using 1.08 unadjusted over-reports airflow in Denver by around twenty percent.
- 7
Residential cooling systems are typically designed for approximately
Explanation
Around 400 cubic feet per minute per ton is the usual design point, often reduced toward 350 in humid climates to improve moisture removal.
- 8
Airflow substantially below 350 cfm per ton risks
Explanation
Less air over the coil means a lower coil temperature. Once it falls below freezing, ice forms and the airflow drops further, which accelerates the problem.
- 9
Airflow substantially above 450 cfm per ton typically causes
Explanation
The thermostat is satisfied on temperature while the house stays damp. It is a common complaint on oversized systems running high blower speeds.
- 10
The evaporator temperature split, or delta-T, is
Explanation
It is a straightforward measurement across the coil, and it is compared against a target that depends on the entering air conditions.