Topic 10 · Service, Airflow & Diagnosis
Set C Questions 21 to 30
- 21
Superheat measured at the condensing unit rather than the evaporator outlet will typically be
Explanation
A long uninsulated suction line through a hot attic can add ten degrees or more. Judging that reading against an evaporator target condemns a healthy system.
- 22
Superheat below about 5 degrees F is dangerous because
Explanation
Liquid cannot be compressed. It washes oil off the bearings and breaks valves, and the damage is often immediate.
- 23
Subcooling below about 3 degrees F indicates
Explanation
A metering device fed with bubbles cannot control flow. Usual causes are undercharge or a restriction upstream of the reading.
- 24
A typical manufacturer target for subcooling on a TXV system is around
Explanation
Eight to twelve degrees is common, but the data plate is the authority and some manufacturers specify quite different figures.
- 25
A run capacitor is tested under load by measuring
Explanation
Capacitance in microfarads equals 2,652 times the amps divided by the volts at 60 hertz. The motor must be running for the test to be valid.
- 26
The usual tolerance on a run capacitor rating is about
Explanation
Six percent is the common figure. Outside it the motor runs less efficiently and hotter, and it is usually the cheapest repair on the unit.
- 27
A failed run capacitor typically causes a motor to
Explanation
Without the phase shift the capacitor provides there is no starting torque. A locked rotor draws very high current until the overload opens.
- 28
The NEMA limit for voltage imbalance on a three phase supply is
Explanation
Two percent, and the limit is tight because a small voltage imbalance produces a current imbalance several times larger.
- 29
Voltage imbalance is calculated as
Explanation
Average the three legs, find the one furthest from the average, and express that gap as a percentage of the average.
- 30
Voltage imbalance damages a motor by
Explanation
A two percent voltage imbalance can produce a current imbalance six to ten times larger, and the extra current becomes heat in the winding.