Increasing blower speed by 20 percent increases the motor power requirement by about
Explanation
Power follows the cube of the speed ratio, and 1.2 cubed is 1.73. This is why the motor nameplate amps are checked before speeding a blower up.
- 42
The friction rate for duct design is calculated from
Explanation
Available static is the blower rating less the coil, filter and accessory losses. Spreading it over the longest effective run gives the rate every duct is then sized to.
- 43
Total effective length includes
Explanation
A single elbow can add the equivalent of many feet of straight duct. Ignoring fittings is why so many systems are designed to a friction rate they never achieve.
- 44
A rectangular duct with a very high aspect ratio, such as 5 to 1, is undesirable because
Explanation
More wall per unit of area means more friction, more sheet metal and more leakage. Aspect ratios beyond about four to one are avoided where possible.
- 45
The most reliable diagnostic sequence when a system is not cooling is to
Explanation
Airflow problems mimic charge problems, so establishing airflow first prevents adding refrigerant to a system whose only fault is a blocked filter.