Topic 07 · Type II: High Pressure Appliances
Set A Questions 1 to 10
- 1
Under 40 CFR 82.152, a high pressure appliance uses a refrigerant whose liquid saturation pressure at 104 degrees F is
Explanation
The classes are defined by saturation pressure at 104 degrees F, not by boiling point. R-22, R-407C, R-410A and R-502 all fall between 170 and 355 psia.
- 2
Which of these is used in a very high pressure appliance?
Explanation
R-13, R-23, R-503 and the R-508 blends all exceed 355 psia at 104 degrees F, or are supercritical there. They appear in cascade low temperature systems and fall under Type II certification.
- 3
Which of these requires Type II certification?
Explanation
Split systems are high pressure appliances charged in the field. Centrifugal machines on R-123 are low pressure and need Type III.
- 4
For a high pressure appliance containing less than 200 pounds of refrigerant, such as an R-22 split system, the required evacuation level is
Explanation
High pressure appliances under 200 pounds require only that the system be brought to atmospheric pressure, whatever their manufacture date. The requirements tighten with charge size and with the date.
- 5
For a high pressure appliance containing 200 pounds or more of refrigerant, and manufactured on or after 15 November 1993, the required evacuation level is
Explanation
Ten inches of mercury vacuum. The same appliance manufactured before that date requires only 4 inches, and a medium pressure appliance of that size requires 15 inches.
- 6
Very high pressure appliances, such as those using R-13, must be evacuated to
Explanation
Bringing it to atmospheric pressure is all that is required, whatever the manufacture date, because the refrigerant will not condense at ordinary recovery cylinder conditions.
- 7
Recovering liquid before vapour on a large high pressure system is preferred because
Explanation
Liquid is several hundred times denser than vapour at the same conditions. Removing it first turns a multi-hour job into a manageable one.
- 8
Push-pull recovery is generally worthwhile on systems containing more than about
Explanation
Below roughly ten to fifteen pounds the setup time outweighs the benefit. Above it, push-pull is dramatically faster than vapour recovery.
- 9
In push-pull recovery, liquid flows from the system to the cylinder because
Explanation
The machine creates the pressure difference and the liquid moves through a separate transfer hose. The machine itself never handles liquid.
- 10
Push-pull recovery should not be used on systems with
Explanation
Without a body of liquid to move there is nothing for push-pull to do, and the setup wastes more time than it saves.