Topic 07 · Type II: High Pressure Appliances
Set B Questions 11 to 20
- 11
A recovery machine that stops or short cycles during recovery may be
Explanation
Recovery machines protect themselves against high discharge pressure. Cooling the cylinder or changing to an empty one usually clears it.
- 12
A thermostatic expansion valve controls
Explanation
The TXV modulates to hold a set superheat. That is why a TXV system is charged by subcooling, not by superheat.
- 13
A system with a TXV is charged by
Explanation
The valve holds superheat constant regardless of charge, so superheat tells you nothing about the charge. Subcooling is the number that responds.
- 14
A system with a fixed orifice or piston is charged by
Explanation
A piston cannot control superheat, so superheat varies with charge and with conditions. The target superheat formula is what makes the reading meaningful.
- 15
Superheat is measured from
Explanation
Superheat is how far above its own boiling point the vapour has been heated. On a blend that boiling point is the dew point.
- 16
Subcooling is measured from
Explanation
Subcooling is how far below its own boiling point the liquid has been cooled, measured from the bubble point on a blend.
- 17
High superheat combined with low subcooling indicates
Explanation
Not enough refrigerant to fill the condenser or feed the evaporator properly. This is the classic undercharge signature.
- 18
High superheat combined with high subcooling indicates
Explanation
Liquid is present but cannot get through. A plugged filter drier or a failed metering device stacks liquid on the high side while starving the coil.
- 19
Low superheat combined with high subcooling indicates
Explanation
Too much refrigerant floods the condenser and overfeeds the evaporator. Continuing to run it risks liquid reaching the compressor.
- 20
Compression ratio is calculated from
Explanation
Both readings must have atmospheric pressure added first. A ratio of two numbers measured from an arbitrary zero has no physical meaning.