Topic 08 · Type III: Low Pressure Chillers
Set A Questions 1 to 10
- 1
Under 40 CFR 82.152, a low pressure appliance uses a refrigerant whose liquid saturation pressure at 104 degrees F is
Explanation
R-11, R-113, R-123 and R-245fa all sit below 45 psia at 104 degrees F. Their saturation pressure is so low that these machines run in a vacuum on the low side at normal operating temperatures.
- 2
Which refrigerant is used in low pressure centrifugal chillers?
Explanation
R-123 replaced R-11 in centrifugal machines. Both are low pressure, and both require Type III certification.
- 3
The required evacuation level for a low pressure appliance is
Explanation
Twenty-five millimetres of mercury absolute is the deepest requirement in the whole table, and it is measured in absolute units rather than as vacuum below atmosphere.
- 4
A low pressure chiller operating normally has a low side pressure that is
Explanation
This single fact drives everything else about Type III work: leaks draw air in rather than pushing refrigerant out.
- 5
Because a low pressure machine runs in a vacuum, a leak on the low side will
Explanation
Air brings moisture, moisture makes acid, and the non-condensables raise condensing pressure. It is why purge units exist on these machines.
- 6
The purpose of a purge unit on a low pressure chiller is to
Explanation
The purge separates non-condensables from refrigerant vapour and expels the air. Its run time is a direct measure of how much the machine is leaking.
- 7
A purge unit running far more often than usual indicates
Explanation
Purge run time is the standard leak indicator on a low pressure machine, and it is logged for exactly that reason.
- 8
A high efficiency purge unit is preferred because it
Explanation
Every purge cycle carries some refrigerant out with the air. High efficiency purges reduce that loss, and EPA regulates purge emissions for this reason.
- 9
During recovery from a low pressure chiller, refrigerant temperature must not be allowed to fall below
Explanation
Water in the chiller or condenser tubes freezes below 32 degrees F, and expanding ice splits the tubes. It is the most expensive mistake available on this equipment.
- 10
Freezing water in the tubes of a low pressure chiller during recovery causes
Explanation
A split tube contaminates the entire refrigerant charge with water and requires retubing. Draining the water side or watching the temperature closely prevents it.