Before recovering from a low pressure machine, the water side should ideally be
Explanation
Moving water resists freezing and carries heat in. Draining removes the risk entirely, at the cost of more work.
A rupture disc on a low pressure chiller typically relieves at approximately
Explanation
These vessels are built for near-atmospheric operation. Fifteen pounds per square inch is enough to burst the disc and lose the charge.
Pressure testing a low pressure chiller must be limited to about
Explanation
Testing must stay below the disc setting. Applying high pressure nitrogen to one of these machines destroys the disc and vents everything inside.
Leak testing a low pressure machine is often done by
Explanation
The machine has to be brought above atmospheric pressure before a leak will show outward at all, but only just above.
Warming a low pressure machine with controlled heat during leak testing works because
Explanation
The saturation pressure of R-123 crosses atmospheric at around 82 degrees F, so gentle warming makes a leak detectable from outside.
Water in a low pressure machine will typically
Explanation
It is also a sign of a tube leak. Both the water and the cause have to be dealt with, and the refrigerant is usually sent for reclaim.
A centrifugal compressor differs from a reciprocating compressor in that it
Explanation
The impeller adds kinetic energy which is then converted to pressure. Its characteristics are what make surge possible.
Surge in a centrifugal chiller is
Explanation
The gas momentarily flows backwards through the impeller. Repeated surging damages bearings and the impeller itself.
Surge is most likely to occur when
Explanation
Low flow against a high pressure difference is exactly the condition the compressor cannot sustain. Fouled condenser tubes make it far more likely.
Fouled condenser tubes on a chiller cause
Explanation
The refrigerant cannot reject heat, so it condenses at a higher temperature. Approach temperature is the measurement that reveals it.