Approach temperature on a chiller is
Explanation
A rising approach means the tubes are transferring heat less well, which normally means fouling. It is the standard trending measurement on a chiller.
R-123 has a lower occupational exposure limit than most refrigerants, which requires
Explanation
The allowable exposure is substantially lower than for R-11 or R-22, so a leak that would be tolerable elsewhere is not tolerable here.
Recovery from a low pressure machine is slow largely because
Explanation
Recovery machines depend on a pressure difference. Low pressure recovery equipment is specifically designed to work with almost none.
Recovery equipment used on low pressure appliances must be
Explanation
High pressure recovery machines cannot reach the required level. The certification is specific to the appliance category.
After recovery from a low pressure chiller, the charge is typically stored
Explanation
These machines hold hundreds or thousands of pounds. A properly rated storage vessel or refrigerant drum is the only practical container.
A hermetic centrifugal chiller motor is typically cooled by
Explanation
Liquid refrigerant carries motor heat away. Any loss of refrigerant flow to the motor therefore risks overheating it.
An oil pump failure on a centrifugal chiller results in
Explanation
High speed journal bearings fail in seconds without oil film. The oil pressure safety trips before that can happen.
Oil in a low pressure chiller is normally
Explanation
The separate oil system is why oil analysis is a routine maintenance item on these machines and a strong predictor of bearing wear.
Oil analysis on a chiller is used to detect
Explanation
Wear metals show bearing deterioration long before a failure, and moisture and acid show that air has been getting in.
Before opening a low pressure machine, the technician must
Explanation
Opening a machine still in a vacuum draws air and moisture straight in, which is the fastest way to contaminate the entire charge.