A low pressure machine left open to atmosphere for an extended period will
Explanation
Large internal surfaces absorb moisture readily. This is why extended evacuation is standard before recharging one of these machines.
Evacuating a low pressure machine after service is done to
Explanation
The vessel volume is enormous, so evacuation takes far longer than on a split system. Rushing it leaves moisture that will form acid.
Which of these tasks requires Type III certification?
Explanation
R-123 is a low pressure refrigerant, so Type III is the required certification. The other three fall under Type I or Type II.
A refrigerant monitor in a chiller machinery room is required primarily to
Explanation
It protects people. With R-123's low exposure limit, a leak that would be a nuisance elsewhere is a genuine health hazard here.
The relief device on a low pressure machine vents to
Explanation
Venting into the room would fill the space with refrigerant. Vent line sizing is covered by ASHRAE 15 and is checked during commissioning.
Charging a low pressure machine is normally done
Explanation
The same freezing hazard applies during charging as during recovery, because evaporating liquid refrigerant absorbs heat from the water side.
A machine that requires frequent purging and shows rising oil acidity is most likely
Explanation
The two symptoms have one cause. Finding and fixing the leak matters more than repeatedly changing the oil.
Chiller log readings are taken regularly because
Explanation
A single reading means little. It is the trend across weeks that shows fouling, leakage or bearing wear developing.
The refrigerant charge of a large centrifugal chiller is typically
Explanation
This is why the leak repair rules, record keeping and recovery equipment requirements all matter so much on these machines.
R-11 was replaced by R-123 in centrifugal chillers because
Explanation
R-123 is an HCFC with far lower ozone depletion potential, though it is itself being phased out under the HCFC schedule.