Topic 08 · Type III: Low Pressure Chillers
Set E Questions 41 to 45
- 41
Retrofitting an R-11 chiller to R-123 typically requires
Explanation
The refrigerants differ enough in capacity and material compatibility that a straight swap does not work. Manufacturer conversion kits exist for this reason.
- 42
The most important single difference between Type II and Type III work is that a low pressure machine
Explanation
Vacuum operation explains the purge unit, the freeze risk, the deep evacuation requirement and the low test pressure all at once.
- 43
When leak testing a low pressure machine with nitrogen, the technician must
Explanation
A nitrogen cylinder holds over two thousand pounds per square inch against a disc that opens at fifteen. The regulator is not optional.
- 44
An electronic leak detector on a low pressure machine in normal operation will
Explanation
Nothing comes out of a leak that is in a vacuum. The machine has to be brought above atmospheric pressure before the detector has anything to find.
- 45
The deepest evacuation requirement in the Section 608 tables, 25 mm Hg absolute, applies to
Explanation
Low pressure appliances require the deepest recovery, because their refrigerant will not leave the machine on its own at any pressure above that.