Topic 07 · Box Fill Calculations
Set A Questions 1 to 10
- 1
What volume allowance is required for one 14 AWG conductor?
Explanation
NEC Table 314.16(B): A 14 AWG conductor requires 2.00 cubic inches.
- 2
What volume allowance is required for one 12 AWG conductor?
Explanation
NEC Table 314.16(B): A 12 AWG conductor requires 2.25 cubic inches.
- 3
What volume allowance is required for one 10 AWG conductor?
Explanation
NEC Table 314.16(B): A 10 AWG conductor requires 2.50 cubic inches.
- 4
A single switch mounted on one yoke counts as how many conductors for box fill?
Explanation
NEC 314.16(B)(4): Each device on a yoke or strap counts as a double volume allowance based on the largest conductor.
- 5
A switch wired with 12 AWG hot/neutral and 14 AWG ground counts as what size for device fill?
Explanation
NEC 314.16(B)(4): Device fill is based on the largest conductor connected to the device, which is the 12 AWG.
- 6
Up to four equipment grounding conductors entering a box count as:
Explanation
NEC 314.16(B)(5): up to four EGCs count as a single volume allowance based on the largest EGC. Each one after the fourth adds a quarter allowance.
- 7
Internal cable clamps in a box count as:
Explanation
NEC 314.16(B)(2): Internal clamps count as one allowance based on the largest conductor in the box.
- 8
Wire nuts and splice connectors count toward box fill as:
Explanation
NEC 314.16(B): Small fittings like wire nuts do not require volume allowance; only count the conductors themselves.
- 9
A conductor entering, spliced, and exiting a box counts as how many?
Explanation
NEC 314.16(B)(1): Count the entering conductor (1) and exiting conductor (1) separately = two total.
- 10
A conductor passing through a box without splicing counts as:
Explanation
NEC 314.16(B)(1): A conductor passing through without splice or termination counts once.