Topic 07 · Box Fill Calculations
Set B Questions 11 to 20
- 11
A pigtail originating and ending in the same box counts as:
Explanation
NEC 314.16(B)(1): Conductors completely within the box are not counted toward fill.
- 12
Standard volume of 4" x 1½" square box is:
Explanation
NEC Table 314.16(A): A 4 x 1-1/2 square box has 21.0 cubic inches.
- 13
Standard volume of 4" x 2⅛" square box is:
Explanation
NEC Table 314.16(A): A 4 x 2-1/8 square box has 30.3 cubic inches.
- 14
Three 12/2 w/G cables enter a 4x4x2⅛ box and connect to one duplex receptacle. Total fill needed is:
Explanation
NEC 314.16: 6 conductors (3×2 for hots/neutrals) = 13.5 cu in; 1 EGC = 2.25 cu in; receptacle = 4.5 cu in. Total = 20.25 cu in.
- 15
A luminaire stud in a box counts as:
Explanation
NEC 314.16(B)(3): Luminaire studs count as one allowance based on the largest conductor in the box.
- 16
A box has 14 AWG switch wires and 12 AWG pass-through wires with clamps. Clamps count as:
Explanation
NEC 314.16(B)(2): Clamp allowance is based on the largest conductor present, which is 12 AWG at 2.25 cu in.
- 17
Each equipment grounding conductor beyond the first four in a box adds:
Explanation
NEC 314.16(B)(5): the first four EGCs share one allowance; each additional EGC or bonding jumper adds a 1/4 volume allowance based on the largest EGC.
- 18
Calculate: 4×10 AWG, 3×12 AWG, 1×10 EGC, 2 clamps in 4x4 box:
Explanation
NEC 314.16: (4×2.5) + (3×2.25) + 2.5 (EGC) + 2.5 (clamps) = 21.75 cu in.
- 19
For straight pulls with 4 AWG+ conductors, box length must be at least _____ times the largest raceway:
Explanation
NEC 314.28(A)(1): Straight pull length = 8 × trade size of largest raceway.
- 20
For angle pulls, distance to opposite wall must be at least _____ times the largest raceway:
Explanation
NEC 314.28(A)(2): Angle pull = (6 × largest) + sum of other raceways on same wall.