Topic 07 · Box Fill Calculations
Set C Questions 21 to 30
- 21
Minimum length for straight pull box with two 3-inch conduits is:
Explanation
NEC 314.28(A)(1): 8 × 3 inches = 24 inches. Additional raceways do not increase length.
- 22
Angle pull box: one 3-inch and two 2-inch conduits entering one wall. Minimum dimension to opposite wall:
Explanation
NEC 314.28(A)(2): (6 × 3) + 2 + 2 = 18 + 4 = 22 inches.
- 23
Distance between raceway entries with same conductors must be at least _____ times the larger raceway:
Explanation
NEC 314.28(A)(2): U-pulls require 6 × trade size of the larger raceway.
- 24
Can nonmetallic box be used with metallic conduit?
Explanation
NEC 314.3 Exception No. 1: Nonmetallic boxes permitted with metal raceways if internal bonding means provide continuity.
- 25
Surface extension from flush box cover requires:
Explanation
NEC 314.22 Exception: Cover must be designed for surface extension; wiring method must be flexible.
- 26
Ceiling luminaire outlet box must support minimum:
Explanation
NEC 314.27(A)(2): Ceiling boxes must support minimum 23 kg (50 pounds).
- 27
Wall-mounted sconce must be independently supported if over:
Explanation
NEC 314.27(A)(1): Unmarked wall boxes support maximum 23 kg (50 pounds).
- 28
Ceiling fan box must be listed and marked for support if fan exceeds:
Explanation
NEC 314.27(C): Paddle fans must have listed box unless under 16 kg (35 lbs) with locking screws.
- 29
Paddle fan over 70 pounds requires:
Explanation
NEC 314.27(C): Fans over 32 kg (70 lbs) must be independently supported from structure.
- 30
Floor boxes for receptacles must be:
Explanation
NEC 314.27(B): Boxes for floor receptacles must be specifically listed for that application.