Topic 07 · Box Fill Calculations
Set D Questions 31 to 40
- 31
Gap around recessed box at drywall finish cannot exceed:
Explanation
NEC 314.21: Noncombustible surfaces around boxes must have no gaps greater than 3 mm (1/8 inch).
- 32
Unused knockout in metal box must be closed to provide:
Explanation
NEC 110.12(A): Unused openings closed with protection substantially equivalent to equipment wall.
- 33
Junction boxes and pull boxes must be installed:
Explanation
NEC 314.29: Boxes must be accessible without removing building parts or excavating.
- 34
Conduit body with splices must have:
Explanation
NEC 314.16(C)(2): Splices allowed in conduit bodies only if marked with volume.
- 35
Do straight-pull and angle-pull rules apply to conduit bodies with 4 AWG+ conductors?
Explanation
NEC 314.28(A)(3): Conduit bodies must comply with straight and angle pull dimensions when handling 4 AWG+ conductors.
- 36
Type NM cable in 2¼" x 4" nonmetallic box without clamp requires:
Explanation
NEC 314.17(C) Exception: NM cable supported within 200mm (8 in.) of box with ¼ inch sheath extension does not need clamp.
- 37
Can a device box be used as a pull box without devices?
Explanation
NEC 314.16: Standard volume calculation applies; device box usable as pull box if conductors do not exceed volume.
- 38
Handhole enclosure is used for:
Explanation
NEC Article 100: Handhole enclosure allows personnel to reach in (but not enter) for maintenance in underground systems.
- 39
Prevent water entry at wet location enclosure raceways using:
Explanation
NEC 314.15: Wet location boxes and fittings must be listed for wet locations; use proper wet-rated connectors.
- 40
Round boxes cannot be used where:
Explanation
NEC 314.2: Round boxes incompatible with locknut/bushing connections due to curved surface.