Topic 07 · Box Fill Calculations
Set E Questions 41 to 50
- 41
Extension rings add their volume to the total box assembly volume for fill calculations:
Explanation
NEC 314.16(A): Extension rings add volume if marked or dimensions are standard per Table 314.16(A).
- 42
4 AWG+ conductors entering enclosure need smooth insulating surface provided by:
Explanation
NEC 300.4(G): 4 AWG+ insulated conductors need smooth rounded insulating surface or substantial insulating material.
- 43
Domed covers add to box volume:
Explanation
NEC 314.16(A): Domed covers add volume if marked by manufacturer or calculated from standard box dimensions.
- 44
Straight pull box with multiple raceways on same wall calculates length as:
Explanation
NEC 314.28(A)(1): Straight pull length = 8 × largest raceway only; additional raceways affect width, not length.
- 45
4 AWG+ conductors opposite removable cover require minimum distance per:
Explanation
NEC 314.28(A)(2) and 312.6(A): Distance determined by table based on wire-bending space requirements.
- 46
Box volume exactly equal to fill allowance is:
Explanation
NEC 314.16: If volume allowance ≤ total box volume, it meets code; no additional margin required.
- 47
Pre-wired assemblies originating and terminating in same box are counted for fill:
Explanation
NEC 314.16(B)(1): Conductors that do not leave the box are not counted in fill calculations.
- 48
Metal boxes must be:
Explanation
NEC 314.4: Metal boxes must be grounded and bonded per Article 250.
- 49
Type NM cable entering metal box must be:
Explanation
NEC 314.17(B): Cable or raceway must be secured to metal box or conduit body.
- 50
Pull box required every _____ of continuous conduit:
Explanation
NEC: No fixed footage limit; restriction is 360 cumulative degrees of bends between pull points.