Set A Questions 1 to 10
- 1
Per NEC 210.3, what is the minimum conductor size for a 15-ampere branch circuit?
Explanation
NEC 210.3 and Table 210.3 require 14 AWG copper minimum for 15-ampere branch circuits.
- 2
Per NEC 210.8(A)(1), which location requires GFCI protection in dwellings?
Explanation
NEC 210.8(A)(1) requires GFCI protection for 125V, 15- and 20-ampere receptacles in bathrooms.
- 3
Per NEC 210.11(C)(1), how many small-appliance circuits must a dwelling kitchen have?
Explanation
NEC 210.11(C)(1) requires a minimum of two 20-ampere small-appliance branch circuits for kitchen receptacles.
- 4
Per NEC 210.23(A)(1), what is the maximum continuous load on a 20A circuit?
Explanation
NEC 210.23(A)(1) limits cord-and-plug loads to 80% of branch-circuit rating; 80% of 20A = 16A.
- 5
Per NEC 210.52(A)(1), what is the maximum distance from a receptacle outlet?
Explanation
NEC 210.52(A)(1) requires no point along the floor line to be more than 6 ft (1.8 m) from a receptacle.
- 6
Per NEC 210.52(C)(1), what is the maximum gap between kitchen countertop receptacles?
Explanation
NEC 210.52(C)(1) requires no more than 24 in. (600 mm) between receptacles measured horizontally.
- 7
Per NEC 210.52(D), where must a bathroom receptacle be located?
Explanation
NEC 210.52(D) requires a receptacle within 36 in. (900 mm) of each bathroom basin.
- 8
Per NEC 210.8(A)(7), what protection is required for laundry area receptacles?
Explanation
NEC 210.8(A)(7) requires GFCI protection for 125V, 15- and 20-ampere receptacles in laundry areas.
- 9
Per NEC 210.12(B), where is AFCI protection required in dwellings?
Explanation
NEC 210.12(B) requires AFCI protection for 120-volt, 15- and 20-ampere circuits in bedrooms, kitchens, family rooms and similar areas. (Before the 2023 NEC this list was in 210.12(A).)
- 10
Per NEC 210.52(E)(1), where must outdoor receptacles be located in dwellings?
Explanation
NEC 210.52(E)(1) requires receptacles at grade level at both front and back of dwellings.