Set B Questions 11 to 20
- 11
Per NEC 210.52(G)(1) and 210.8(A)(2), garage receptacles must be:
Explanation
NEC 210.52(G)(1) and 210.8(A)(2) require at least one GFCI-protected receptacle in each garage.
- 12
Per NEC 210.70(A)(1), what may replace a light fixture in non-kitchen rooms?
Explanation
NEC 210.70(A)(1) Exception No. 1 allows a switched receptacle in habitable rooms other than kitchens and bathrooms.
- 13
Per NEC 220.41, what is the dwelling lighting load calculation?
Explanation
NEC 220.41 sets a unit load of 3 VA per square foot for dwelling general lighting. (Before the 2023 NEC it was in Table 220.12.)
- 14
Per NEC 220.14(I), what VA value is assigned per general-purpose receptacle?
Explanation
NEC 220.14(I) requires general-purpose receptacle outlets in non-dwellings be calculated at 180 VA minimum.
- 15
Per NEC 210.52(C)(4), what is the minimum countertop width for a receptacle?
Explanation
NEC 210.52(C)(4) requires a receptacle at any countertop space 12 in. (300 mm) or wider.
- 16
Per NEC 210.11(C)(3), what is the minimum bathroom circuit rating in dwellings?
Explanation
NEC 210.11(C)(3) requires a minimum 20-ampere branch circuit for bathroom receptacle outlets.
- 17
Per NEC 210.21(B)(1), a single receptacle rating must be:
Explanation
NEC 210.21(B)(1) requires receptacle rating not less than the branch-circuit rating.
- 18
Per NEC Table 210.21(B)(3), what is the maximum rating on a 20A circuit?
Explanation
NEC Table 210.21(B)(3) allows 15- and 20-ampere receptacles on a 20-ampere branch circuit.
- 19
Per NEC 210.52(H), what distance applies to HVAC equipment receptacles?
Explanation
NEC 210.52(H) requires a receptacle within 25 ft (7.5 m) of HVAC equipment.
- 20
Per NEC 210.8(A)(5), which basement receptacles need GFCI protection?
Explanation
NEC 210.8(A)(5) requires GFCI protection for receptacles in dwelling unit basements. Since the 2020 NEC that means the whole basement, finished or not, not only the unfinished part.