Set C Questions 21 to 30
- 21
Per NEC 210.52(A)(2)(1), what is the minimum wall space width defined?
Explanation
NEC 210.52(A)(2)(1) defines wall space as 2 ft (600 mm) or more unbroken width.
- 22
Per NEC 210.8(B), where is GFCI required in non-dwelling places?
Explanation
NEC 210.8(B) requires GFCI in commercial kitchens, bathrooms, rooftops, and wet areas.
- 23
Per NEC 210.4(B), multiwire circuits require disconnecting:
Explanation
NEC 210.4(B) requires simultaneous disconnection of all ungrounded conductors at the origin.
- 24
Per NEC 210.19(A)(1), conductor ampacity must be:
Explanation
NEC 210.19(A)(1) requires conductor ampacity not less than the maximum load served.
- 25
Per NEC 210.19(A)(1), continuous loads require ampacity of:
Explanation
NEC 210.19(A)(1) requires ampacity at 125% of continuous load plus 100% noncontinuous.
- 26
Per NEC 210.11(C)(2), how many laundry circuits are required?
Explanation
NEC 210.11(C)(2) requires at least one 20-ampere circuit for laundry receptacles.
- 27
Per NEC 210.52(F), which hallway needs a receptacle outlet?
Explanation
NEC 210.52(F) requires receptacle in hallways 10 ft (3.0 m) or more in length.
- 28
Per NEC 210.8(A)(4), where is GFCI required below grade?
Explanation
NEC 210.8(A)(4) requires GFCI for 125V receptacles in crawl spaces at or below grade.
- 29
Per NEC 210.20(A), a 15-ampere circuit maximum continuous load is:
Explanation
NEC 210.20(A) limits continuous loads to 80% of branch rating; 80% of 15A = 12A.
- 30
Per NEC 210.70(A)(2)(a), where is exterior lighting required?
Explanation
NEC 210.70(A)(2)(a) requires lighting outlet at each grade-level outdoor entrance.