Set D Questions 31 to 40
- 31
Per NEC 210.52(C)(2), what are the island countertop minimums?
Explanation
NEC 210.52(C)(2) requires receptacles on island countertops 24 in. x 12 in. or larger.
- 32
Per NEC 210.8(F), dishwasher GFCI applies to circuits:
Explanation
NEC 210.8(F) requires GFCI for dishwasher circuits rated 150V or less to ground.
- 33
Per NEC 210.52(B)(1), small appliance circuits serve:
Explanation
NEC 210.52(B)(1) requires small-appliance circuits for kitchen, pantry, dining room areas.
- 34
Per NEC 210.52(B)(2), what receptacle is allowed on small-appliance circuits?
Explanation
NEC 210.52(B)(2) Exception 2 permits refrigerator receptacles on small-appliance circuits.
- 35
Per NEC 220.52(A), how much VA per small-appliance circuit?
Explanation
NEC 220.52(A) requires calculating each small-appliance circuit at 1,500 VA for feeder load.
- 36
Per NEC 220.52(B), what laundry load is added for dwellings?
Explanation
NEC 220.52(B) adds minimum 1,500 VA for laundry circuit in dwelling feeder calculations.
- 37
Per NEC 210.20(A), overcurrent device rating must be:
Explanation
NEC 210.20(A) requires overcurrent rating at 125% continuous plus 100% noncontinuous loads.
- 38
Per NEC 210.23(B), a 30A circuit maximum cord load is:
Explanation
NEC 210.23(B) limits cord-and-plug loads on 30A circuits to 80%; 80% of 30A = 24A.
- 39
Per NEC 210.25(A), dwelling circuits may supply loads:
Explanation
NEC 210.25(A) requires dwelling unit circuits to supply only loads within that unit.
- 40
Per NEC 210.52(C)(2), peninsular countertop minimums are:
Explanation
NEC 210.52(C)(2) requires receptacles on peninsular countertops 24 in. x 12 in. or larger.